How To Set Up WisBlock Kit 4 and RAK Edge Gateway - Complete LoRaWAN Guide with TTN V3 and Qubitro

KHM-028-00.png

Overview

This guide is about learning how to set up a complete LoRaWAN application from the device and gateway up to the network server.

This guide is composed of the following sections:

📝 NOTE: If you are new to LoRaWAN, here are a few good references about LoRaWAN and gateways:

LoRaWAN gateway models like WisGate Edge have built-in network servers. It is also common that the LoRaWAN network server is external or in the cloud. The popular LoRaWAN network server in the cloud that you can use for free (but offers enterprise service, too) is TTN.

Setting Up the Gateway

WisGate Edge is the RAK flagship line of commercial-grade gateways. Gateways from this product line are designed to work either indoor or outdoor, customizable in terms of the backhaul connectivity options, antenna type, and power provisioning. Here are the products that you may look to as you build your LPWAN base station:

Configuring the WisGate Edge Gateway

This section will guide you on how to set up your WisGate Edge Gateway.

📝 NOTE: In this tutorial, RAK7268 WisGate Edge Lite 2 will be used. In powering and assembling the gateway, you may look for the Quick Start Guide of the WisGate Edge Gateways.

Access the Gateway

In this section, several ways of accessing the gateway are provided to have different alternatives for you to choose from depending on the availability of the requirements needed.

⚠️ WARNING: Do not power the device if the LoRa Antenna port has been left open to avoid potential damage to the RAK7268/RAK7268C WisGate Edge Lite 2.

Wi-Fi AP Mode

By default, the gateway will work in Wi-Fi AP Mode, which means that you can find an SSID named RAK72XX_YYYY on your PC's Wi-Fi Network List. XX is the code of your chosen WisGate Edge Gateway and YYYY is the last two bytes of the gateway's MAC address.

📝 NOTE: No password is required to connect via Wi-Fi.

Using your preferred Web browser, log in with the credentials provided below:

  • Browser Address: 192.168.230.1
  • Username: root
  • Password: root

WAN Port (Ethernet)

Connect the Ethernet cable to the port marked ETH on the gateway and the other end to the PoE port of the PoE injector. Connect the LAN port of the PoE injector to your PC.

The default IP is 169.254.X.X. The last two segments (X.X) are mapped from the last four bits of the MAC address of your gateway.

For example, the last four bits of the MAC address are 0F:01, and the IP address is 169.254.15.1. Make sure to manually set the address of your PC to one in the same network (for example, 169.254.15.100). Use the same credentials for the Web UI as for AP mode.

KHM-028-01.png

Setting Up the Network Server

Registering RAK7268 WisGate Edge Lite 2 to TTNv3

This section shows how to connect the RAK7268 WisGate Edge Lite 2 to TTNv3.

If you don’t have a TTN account, create an account first. Click the Sign up button, then log in.

KHM-028-02.png

Make sure first you are in the right TTN cluster. Use your The Things ID credentials to log in. In this example, choose Europe 1.

KHM-028-03.png

KHM-028-04.png

After you have logged in, you need to register your commercial gateway to TTNv3. To register, choose Go to gateways. If you have already registered your gateways before, head on to Gateways > + Add gateway.

KHM-028-05.png

Fill in the needed information:

  • Owner – Automatically filled by The Things Stack, based on your account or created Organization.
  • Gateway ID – This will be the unique ID of your gateway in the Network. ID must contain only lowercase letters, numbers, and dashes (-).
  • Gateway EUI - A 64 bit extended unique identifier for your gateway. This is where the gateway you get on the above section Configuring the RAK7268 WisGate Edge Lite 2.
  • Gateway name – A name for your gateway.
  • Gateway description (optional) - Optional gateway description; can also be used to save notes about the gateway.
  • Gateway Server address - The address of the gateway server to connect to.
  • Frequency plan - The frequency plan used by the gateway.
📝 NOTE:
  • There are three server clusters available for TTN V3. In this guide, you will use eu1.cloud.thethings.network. You need to select the closes one in your country or location for optimized performance.

  • The available TTN V3 clusters are:

    - North American Region - `nam1.cloud.thethings.network`
    - European Region - `eu1.cloud.thethings.network`
    - Australian Region - `au1.cloud.thethings.network`
    
  • Also, you will be using Europe 863-870 MHz (SF9 for RX2 - recommended).

KHM-028-06.png

KHM-028-07.png

TTNv3 supports TLS server authentication and Client token, which requires a trust file and a key file to configure the gateway and successfully connect it to the network. Generating the token for the gateway is the next step in this guide. To generate a key file, from the Overview page of the registered gateway, navigate to API keys.

KHM-028-08.png

On the API keys page, choose + Add API key.

KHM-028-09.png

In the Name field, type the name of your key (for example - mykey). Choose Grant individual rights and select Link as Gateway to a Gateway for traffic exchange, i.e. read uplink and write downlink.

KHM-028-010.png

To generate the key, choose the Create API key. The following window will pop up, telling you to copy the key you just generated.

KHM-028-011.png

⚠️ WARNING: Copy the key and save it in a .txt file (or other), because you won’t be able to view or copy your key after that.

KHM-028-012.png

KHM-028-013.png

Click I have copied the key to proceed.

KHM-028-014.png

Configure the gateway to connect it successfully to the TTN V3 Server. To configure the gateway, access it via the Web UI. To learn how to do that, check out the RAK7268 Quick Start Guide.

KHM-028-015.png

Navigate to LoRa Network > Network Settings > Mode drop-down menu, then choose Basics Station.

KHM-028-016.png

Select Switch mode to apply the change. After that, the Basics Station Configuration pane settings will show up. To connect the gateway to TTNv3, the following parameters must be configured:

  • Server – For server, choose LNS Server.
  • URI – This is the link to The Things Stack server. Note that, for this tutorial, you are connecting the gateway to the European cluster. For Europe, fill in the following: wss://eu1.cloud.thethings.network.
  • Port – The LNS Server uses port 8887. Type in 8887.
  • Authentication Mode – Choose TLS server authentication and Client token. When selected, the trust and the token field will show up.
  • trust – For trust, you will use the Let’s Encrypt ISRG ROOT X1 Trust certificate. Download the certificate first.
  • token - This is the generated API key. The key must start with Authorization:. Example:
Authorization: YOUR_API_KEY
📝 NOTE: Replace YOUR_API_KEY with the key generated previously. Have in mind that there should be a “space” between Authorization: and YOUR_API_KEY, as shown in Figure 17.

KHM-028-017.png

To save the changes, click Save & Apply.

You can now see that your gateway is connected to TTNv3 as Basics Station:

KHM-028-018.png

Setting Up the Device

Connecting RAK4631 to TTN V3 Application

Now that you are logged in to the platform, the next step is to create an application. In your console, click Create an application.

KHM-028-019.png

To have an application registered, input first the specific details and necessary information about your application, then click Create application.

KHM-028-020.png

If you had no error during the previous step, you should now be on the application console page. The next step is to add end-devices to your TTN application.

LoRaWAN specification enforces that each end-device has to be personalized and activated. There are two options for registering devices depending on the activation mode you select. Activation can be done either via Over-The-Air-Activation (OTAA) or Activation-By-Personalization (ABP). Click + Add end device, as shown in Figure 21.

KHM-028-021.png

To register the module, click Manually first.

KHM-028-022.png

Choose the following configurations in adding the end devices.

KHM-028-023.png

Click Show advanced activation, LoRaWAN class, and cluster settings, then select Over the air action (OTAA).

KHM-028-024.png

Then input a unique End device ID and EUIs (DevEUI and AppEUI), as shown in Figure 25. Check if the sticker on the RAK4631 module has a DevEUI or a QR code that you can scan, then use this as the device unique DevEUI. For AppEUI, use 00 00 00 00 00 00 00 01 instead of Fill with Zeros button (there are LoRa modules that do not support all zero APPEUI). For the AppKey, you can click the Generate button. Finally, click Register End Device.

KHM-028-025.png

You should now be able to see the device on the TTN console after you fully register your device, as shown in Figure 26. Take note of these keys, such as the AppEUI, DevEUI, and the AppKey, as they are needed in the next part of this guide.

KHM-028-026.png

Creating Environment Monitoring Application

Hardware Setup

This section is about the actual device configuration.

RAK1906 WisBlock Environmental Sensor Module can be connected to any slot of RAK5005-O WisBlock Base Board to communicate with the RAK4631 WisBlock LPWAN Module. It will work on SLOT A to D. Also, always secure the connection of the WisBlock module by using compatible screws.

KHM-028-027.png

Assembling and Disassembling of WisBlock Modules

Assembling

As shown in Figure 28, the location for Slots A, B, C, and D are properly marked by silkscreen. Slots C and D are located on the bottom of WisBlock Base. Follow carefully the procedure defined in RAK5005-O module assembly/disassembly instructions to attach a WisBlock module. Once attached, carefully fix the module with an M1.2 x 3 mm screw.

KHM-028-028.png

Disassembling

The procedure for disassembling any type of WisBlock module is the same.

First, remove the screws.

KHM-028-029.png

Once the screws are removed, check the silkscreen of the module to find the correct location where force can be applied.

KHM-028-030.png

Apply force to the module at the position of the connector, as shown in Figure 31, to detach the module from the baseboard.

KHM-028-031.png

📝 NOTE: If you will connect other modules to the remaining WisBlock Base slots, check on the WisBlock Pin Mapper tool for possible conflicts. RAK1906 uses I2C communication lines, and it can cause possible conflict, especially on some IO modules.

LoRa and BLE Antenna

Another important part component of RAK4631 is the antennas.

KHM-028-032.png

KHM-028-033.png

You need to ensure that the antenna is properly connected to have a good LoRa signal. Do not power the module without an antenna connected to the IPEX connector to avoid damage to the RF section of the chip.

RAK4631 has a label on its sticker on where to connect the antennas, as shown in Figure 34.

KHM-028-034.png

📝 NOTE: Detailed information about the RAK4631 BLE and LoRa antenna can be found on the antenna datasheet.

 

⚠️ WARNING: When using the LoRa or Bluetooth Low Energy transceivers, make sure that an antenna is always connected. Using these transceivers without an antenna can damage the system. Make sure to fix the module with the screws to ensure a proper function.

After all this setup, you can now connect the battery (optional) and USB cable to start programming the RAK1906.

⚠️ WARNING:
  • Battery can cause harm if not handled properly.
  • Only 3.7-4.2 V Rechargeable LiPo batteries are supported. It is highly recommended not to use other types of batteries with the system unless you know what you are doing.
  • If a non-rechargeable battery is used, it has to be unplugged first before connecting the USB cable to the USB port of the board to configure the device. Not doing so might damage the battery or cause a fire.
  • Make sure the battery wires match the polarity on the RAK WisBlock Base Board. Not all batteries have the same wiring.
  • Only 5 V solar panels are supported. Do not use 12 V solar panels. It will destroy the charging unit and eventually other electronic parts.

Software Setup

The RAK1906 is a 4-in-1 Environmental Sensor board that contains the Bosch BME680 chip. It is specially designed for wearables where size and low power consumption are critical requirements. The BME680 contains a small Metal-Oxide (MOX) sensor and an I2C interface used to communicate with WisBlock Core.

The RAK1906 module gives information about:

  • Air pressure
  • Air quality
  • Ambient Air Temperature
  • Environment Humidity
⚠️ WARNING: The BME680 requires a burn-in period to collect accurate readings. The burn-in procedure can be achieved by reading all sensors once every 5 seconds for at least 20 minutes the first time that you use it. For each subsequent use, the readings should stabilize 2-3 minutes after power-up.

Software Configuration

Download the Arduino IDE, then install it on your PC or laptop.

⚠️ WARNING: If you are using Windows 10. Do NOT install the Arduino IDE from the Microsoft App Store. Install the original Arduino IDE from the Arduino official website! The Arduino app from the Microsoft App Store has problems using third-party Board Support Packages.

KHM-028-035.png

KHM-028-036.png

KHM-028-037.png

KHM-028-038.png

Open the Arduino IDE, then install the RAKwireless BSP support for the Arduino Board Manager.

Click on File > Preferences. In the Preferences window, look for Additional Boards Manager URLs, then click the icon on the right side.

KHM-028-039.png

KHM-028-040.png

Copy https://raw.githubusercontent.com/RAKwireless/RAKwireless-Arduino-BSP-Index/main/package_rakwireless_index.json, paste it into the new window, then click OK > OK.

KHM-028-041.png

KHM-028-042.png

Go to Tools > Board: "Arduino Uno" > Boards Manager. Type RAK in the search bar and the RAKwireless Core modules will be shown in the window.

KHM-028-043.png

KHM-028-044.png

Choose RAKwireless nRF Boards, then Install. After installing the core nRF core module, click Close.

KHM-028-045.png

After the installation of the RAKwireless nRF Board core module, you can get the program by navigating on the example code, as shown in Figure 46. Open it on the Arduino IDE, and save it as Environment_Monitoring.ino.

KHM-028-046.png

Once the example code is open, install the Adafruit BME680 library, SX126x Arduino library, and the U8g2lib Library, by clicking the links highlighted in red. You will be directed to Arduino Library Manager for each link you will be clicking.

KHM-028-047.png

During the installation, you will be asked to install the Adafruit Unified Sensor library. Install it, as well.

KHM-028-048.png

Configuring LoRaWAN

Before uploading the Arduino Code, there are configurations that you need to set up to ensure that the device can join a LoRaWAN Network server.

The steps below will explain the default settings and how to configure them.

Set up the LoRa Region.

Default region is EU868.

LoRaMacRegion_t g_CurrentRegion = LORAMAC_REGION_EU868;

You can change this to a region that is applicable to you like LORAMAC_REGION_US915, LORAMAC_REGION_AU915, etc.

Set up the LoRaWAN activation method.

Default is OTAA.

bool doOTAA = true;

To configure the device to ABP, you need to make this boolean variable false.

Set up the message type if confirmed or not.

Default is confirmed message.

lmh_confirm g_CurrentConfirm = LMH_CONFIRMED_MSG;

You can change to an unconfirmed message by changing the value to LMH_UNCONFIRMED_MSG.

Set up device class.

Default is Class A.

DeviceClass_t g_CurrentClass = CLASS_A;

You can change this to CLASS_B (still under development) or CLASS_C.

Setup the EUIs and KEY. Get these parameters from the Connecting RAK4631 to TTN V3 Application section of this guide. It is very important that the EUI and KEY will match the one configured in the TTN application. Otherwise, your device will not be able to connect to the TTN server. In this application, the device is activated via OTAA so you need to configure the Device EUI, Application EUI, and Application Key.

uint8_t nodeDeviceEUI[8] = {0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x33, 0x33};
uint8_t nodeAppEUI[8] = {0xB8, 0x27, 0xEB, 0xFF, 0xFE, 0x39, 0x00, 0x00};
uint8_t nodeAppKey[16] = {0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88, 0x88};

Set up uplink period.

The default is 20000 mS.

#define LORAWAN_APP_INTERVAL 20000

LoRaWAN Payload

  • This is the setup on the void send_lora_frame(void) function.
if (lmh_join_status_get() != LMH_SET)
{
  //Not joined, try again later
  return;
}
if (!bme.performReading()) {
  return;
}
bme680_get();

lmh_error_status error = lmh_send(&m_lora_app_data, g_CurrentConfirm);
if (error == LMH_SUCCESS)
{
  count++;
  Serial.printf("lmh_send ok count %d\n", count);
}
else
{
  count_fail++;
  Serial.printf("lmh_send fail count %d\n", count_fail);
}
  • This is the setup on the void bme680_get() function. This will gather the data from the sensor and package them in a LoRaWAN payload.
char oled_data[32] = {0};
Serial.print("result: ");
uint32_t i = 0;
memset(m_lora_app_data.buffer, 0, LORAWAN_APP_DATA_BUFF_SIZE);
m_lora_app_data.port = gAppPort;

double temp = bme.temperature;
double pres = bme.pressure / 100.0;
double hum = bme.humidity;
uint32_t gas = bme.gas_resistance;

data = "Tem:" + String(temp) + "C " + "Hum:" + String(hum) + "% " + "Pres:" + String(pres) + "KPa " + "Gas:" + String(gas) + "Ohms";
Serial.println(data);

// display bme680 sensor data on OLED
u8g2.clearBuffer();         // clear the internal memory
u8g2.setFont(u8g2_font_ncenB10_tr); // choose a suitable font

memset(oled_data, 0, sizeof(oled_data));
sprintf(oled_data, "T=%.2fC", temp);
u8g2.drawStr(3, 15, oled_data);

memset(oled_data, 0, sizeof(oled_data));
sprintf(oled_data, 64, "RH=%.2f%%", hum);
u8g2.drawStr(3, 30, oled_data);

memset(oled_data, 0, sizeof(oled_data));
sprintf(oled_data, "P=%.2fhPa", pres);
u8g2.drawStr(3, 45, oled_data);

memset(oled_data, 0, sizeof(oled_data));
sprintf(oled_data, "G=%dOhms", gas);
u8g2.drawStr(3, 60, oled_data);

u8g2.sendBuffer(); // transfer internal memory to the display

uint16_t t = temp * 100;
uint16_t h = hum * 100;
uint32_t pre = pres * 100;

//result: T=28.25C, RH=50.00%, P=958.57hPa, G=100406 Ohms
m_lora_app_data.buffer[i++] = 0x01;
m_lora_app_data.buffer[i++] = (uint8_t)(t >> 8);
m_lora_app_data.buffer[i++] = (uint8_t)t;
m_lora_app_data.buffer[i++] = (uint8_t)(h >> 8);
m_lora_app_data.buffer[i++] = (uint8_t)h;
m_lora_app_data.buffer[i++] = (uint8_t)((pre & 0xFF000000) >> 24);
m_lora_app_data.buffer[i++] = (uint8_t)((pre & 0x00FF0000) >> 16);
m_lora_app_data.buffer[i++] = (uint8_t)((pre & 0x0000FF00) >> 8);
m_lora_app_data.buffer[i++] = (uint8_t)(pre & 0x000000FF);
m_lora_app_data.buffer[i++] = (uint8_t)((gas & 0xFF000000) >> 24);
m_lora_app_data.buffer[i++] = (uint8_t)((gas & 0x00FF0000) >> 16);
m_lora_app_data.buffer[i++] = (uint8_t)((gas & 0x0000FF00) >> 8);
m_lora_app_data.buffer[i++] = (uint8_t)(gas & 0x000000FF);
m_lora_app_data.buffsize = i;

Data Format

Byte1 Byte2 Byte3 Byte4 Byte5
1 Temperature1 Temperature2 Humidity1 Humidity2
Byte6 Byte7 Byte8 Byte9 Byte10 Byte11 Byte12 Byte13
Barometric1 Barometric2 Barometric3 Barometric4 Gas1 Gas2 Gas3 Gas4
  • Byte1 is a marker for the data type, here always 1.
  • Every byte value is MSB first.
  • Temperature is sent as two bytes, enlarged 100 times for accuracy. For example, 2510 means 25.01 C, sent as 0x09 0xCE.
  • Humidity is sent as two bytes, enlarged 100 times for accuracy. For example, 4173 means 41.73%, sent as 0x10 0x4D.
  • Barometric pressure is sent as four bytes, enlarged 100 times for accuracy. For example, 100945 means 1009.45 hPa, sent as 0x00 0x01 0x8A 0x51.
  • Gas resistance is sent as four bytes. For example, 63560 Ohm, sent as 0x00 0x00 0xF8 0x48.

Uploading the Arduino Code

After a successful installation of the library and configuration of the LoRaWan Network Server setup, you can now select the right serial port and upload the code, as shown in Figure 49 and Figure 50.

KHM-028-049.png

KHM-028-050.png

When you have successfully uploaded the example sketch, open the serial monitor of the Arduino IDE to see the sensor's reading logs. If you see the logs, as shown below, then your RAK1906 is properly communicating to the WisBlock core.

10:30:07.777 -> =====================================
10:30:07.777 -> Welcome to RAK4630 LoRaWan!!!
10:30:07.777 -> Type: OTAA
10:30:07.777 -> Region: EU868
10:30:07.777 -> =====================================
10:30:07.777 -> Chip ID=0x61
10:30:12.974 -> OTAA Mode, Network Joined!
10:30:33.999 -> Sending frame now...
10:30:33.999 -> result: Tem:28.70C Hum:67.00% Pres:948.50KPa Gas:27646Ohms
10:30:33.999 -> lmh_send ok count 1
10:30:53.979 -> Sending frame now...
10:30:53.979 -> result: Tem:28.70C Hum:67.00% Pres:948.50KPa Gas:242488Ohms
10:30:54.012 -> lmh_send ok count 2
10:31:14.006 -> Sending frame now...
10:31:14.006 -> result: Tem:28.70C Hum:67.00% Pres:948.50KPa Gas:457174Ohms
10:31:14.006 -> lmh_send ok count 3
10:31:33.997 -> Sending frame now...
10:31:33.997 -> result: Tem:28.69C Hum:67.00% Pres:948.50KPa Gas:74102Ohms
10:31:34.032 -> lmh_send ok count 4

Setting Up IoT Dashboard Using Qubitro

This section will guide you on how to integrate your application using Qubitro.

Go to Qubitro Portal and create your account.

KHM-028-051.png

Login into your Qubitro account. Click New Project, then fill out your desired Project Name as well as the Project Description, then click Create.

KHM-028-052.png

Then click Add source.

KHM-028-053.png

Choose The Things Stack, then click Continue.

KHM-028-054.png

For the Connection, copy and paste the Project ID and Webhook signing key to notepad. These credentials will be used in the later part, then click Done.

KHM-028-055.png

KHM-028-056.png

Head on to the TTN Application console to add the Webhook to it.

KHM-028-057.png

Click your device then go to Integrations > Webhooks > Add webhook.

KHM-028-058.png

KHM-028-059.png

Choose Qubitro as your webhook template.

KHM-028-060.png

KHM-028-061.png

Fill in the needed details:

  • Webhook ID – For this example, you may use environment-monitoring.
  • Project ID – Paste the credential you copied from Step 5.
  • Webhook signing key – Paste the credential you copied from Step 5.

Then click Create Qubitro webhook.

KHM-028-062.png

KHM-028-063.png

After creating your webhook, go back to your Qubitro platform to check the changes made.

KHM-028-064.png

Refresh the Qubitro platform and the newly-added device is now included in the platform.

KHM-028-065.png

KHM-028-066.png

Click Formatter to include the decoder for Temperature and Humidity as an example of showing these measurements on the platform.

KHM-028-067.png

Copy the decoder code below and paste it inside the Formatter > Uplink, then click Save.

function decodeUplink(input) {
  return {
    data: {
      temperature : (input.bytes[1] << 8 | (input.bytes[2])) / 100,
      humidity : (input.bytes[3] << 8 | (input.bytes[4])) / 100
    },
    warnings: [],
    errors: []
  };
}

Click the Data tab. It should show the latest data by clicking the Refresh button.

KHM-028-068.png

Once done, click Analytics, then click + Add chart to add the graph for Temperature and Humidity.

KHM-028-069.png

KHM-028-070.png

Once done, tick both temperature and humidity, and choose Line under them. You may use Environment Monitoring as your Chart name, then click Create chart.

KHM-028-071.png

KHM-028-072.png

Then there you have it, the Environment Monitoring graph for Temperature and Humidity.

KHM-028-073.png

Updated